PWM Control of electric Waterpump

Does anyone have an idea how I can control my electric water pump using PWM?

Regardless of the cooling water temperature, the pump should always run at at least 50%. From a cooling water temperature of 80 ° C, the pump should go to 60% and then the speed should be increased by 10% for every 5 °C increase in the water temperature.

I am not sure which values have to be entered in the variable mapping. Many thanks

Carsten

319 Views
George Stokes
George Stokes
Jul 09, 2021

No it wont matter. What you will see is that below -50, the duty cycle will be 0%. Between -50 and 80, the duty cycle will vary from 40% to 50%. Above 80, the duty cycle will increase 10% for every 5 degrees. If 50% is the minimum you would like to see, then set the 50% duty cycle value to -50 also and set the 60% duty cycle value to 80.